Hello SOble, If you only use S7 PUT / GET communication you do not need to create an S7 connection in the S7-300 cpu. The S7-300 cpu is working as server and you create the connection and programming (PUT and GET) in the S7-1200 cpu. You may want to look in the document: CPU-CPU Communication with SIMATIC Controllers |