5/7/2011 4:42 AM | |
Joined: 6/7/2010 Last visit: 7/9/2024 Posts: 571 Rating:
HI I am using setpoint exchange in 840D, For that I have enabledthe optionalbit .And logic has been written & parameters has done . But still Setpoint is not exchanged from one axis to another.( DB41.dbx96.5 is not getting high )Find the attached logic. Could any one suggest?
AttachmentFC100.pdf (212 Downloads) |
5/10/2011 6:57 PM | |
Thanks for Suggesion.... I got the set point Exchange. |
Regards, |
5/12/2011 7:54 AM | |
Posts: 2964 Rating:
Hello.... What exactly have corrected for working the setpoint exchangeproperly ??? your answer may help others in solving... Regards, Ekalavya |
5/15/2011 8:12 AM | |
Hi, Clearly i can't find the problem, But when i tried with X axis the setpoint has been exchanged ( with same logic ).After i tried with Spindle the problem sloved. I dont know why first the setpoint is not exchanged from Spindle.So i have planed to clear all the data from the system and then check the Spindle Setpoint exchange from First & come back with the solution.........And find the attachement Example of the Setpoint Exchange with Sample logic..it may help some one... AttachmentSetpoint Exchange.pdf (268 Downloads) |
Regards, |
5/16/2011 6:36 AM | |
Posts: 2964 Rating:
Hello....Muthamil_S Thanks for detailed infromation.....it is really useful.....if some is doing the setpoint exchange..... Regards, Ekalavya |