Hi Gengus, It is very easy, just program the first time one byte output on system A and one byte input in system B. The DP/DP-coupler is for both systems a slave. When it is the new coupler then the first bit in the first byte can be used to look if the other system is working well (something like a alive bit). This can be chosen with the dipswitches on the coupler. When that is working you might couple 2 and 4 bytes also easy, therefore are some commands to read them out like "L IW..." "L ID..." when you want to do 3 bytes or more then 4 bytes then you have to use SFC14 and SFC15 to get the data at onces into the CPU. When it is in the PII or the PIQ then it is not necessarry to use SFC14/15. Please also see the handbook: DP/DP Couplerfor further information about the dipswitches and so on.... |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|
6/15/2008 5:14 PM | |
Joined: 12/22/2006 Last visit: 1/25/2022 Posts: 1742 Rating: (308) |
Hello all together There is an interesting FAQ about consistency of data in distributed IO in general (a DP/DP coupler is just one possibility among others). http://support.automation.siemens.com/WW/view/en/28991143 Download the "description" from the site, and you will have a good idea what consistent data is. You will see alsoa lot of other entries about consistent data. I hope this help. |
Last edited by: edr at: 6/15/2008 5:21 PMBest regards |
|