12/4/2013 9:55 AM | |
Posts: 3 Rating:
|
For setup PPO5 for the Altivar drive, u require GSD file of drive, After installing GSD file in TIA portal, u can easily configure PPO5. |
10/29/2014 11:11 PM | |
Joined: 9/27/2006 Last visit: 4/19/2025 Posts: 12346 Rating:
|
Hello Tazz; PPO5 is defined as 4PKW (read/write acyclic) + 10 PZD (read/write cyclic), a total of 28 bytes reserved for exchanges with the drive. It seems to me that you can use selection #2 of the Altivar drive (Periodic(10-10) Aperiodic(4-4)) to implement PPO5. Please have a look at the following discussion for more hints: Profibus communication between Altivar61 And S7416-3 DP Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 10/30/2014 1:14 AMLast edited by: dchartier at: 10/29/2014 11:14 PM |
|
10/30/2014 7:24 AM | |
Joined: 12/10/2010 Last visit: 2/23/2025 Posts: 2 Rating:
|
It seems the problem was with tele09.gsd file for altivar 71. Tried with other one tele0965.gsd and now it working. I attached it for others thx for help
Attachmentatv71_61.zip (677 Downloads) |
This contribution was helpful to
1 thankful Users |