Hello wreng assuming you operate your Profibus at a half decent speed (let's say 500Kbsor1.5Mbs) it's update time will have an insignificant effect on your serial comms. The problem will most likely lie in the fact that P_SEND and P_RCV use SFB52/53 internally. Please check this by right clicking on them, open the Object Properties and go to the "Calls" tab (I don't have them in my current Step7 install and can't verify this). If SFB52/53 or SFC58/59 are listed as being called from them, you will only be able to have a certain number of simultaneously active callswhich would explain the "long" execution time of all 26 comms job. How many simultaneously active calls are supported is CPU dependant and explained in the FAQ below: What restrictions are there for active jobs when communicating with SFC 58 / SFC 59 and SFB 52 / SFB 53 via PROFIBUS DP and PROFINET IO? I hope this helps and please let us know what you find. |