9/14/2016 8:37 PM | |
Posts: 13 Rating: (0) |
have almost same problem, after i download the program to the PLC i get an SF error on my PM-E module. notice that i have more than 5 same modules only this give the error. (6ES7138-4CA01-OAAO). i check wiring seems to be fine, even i place an other module give same problem. When i run hardware diagnostics i get the message of possible couse off the problem. there is a channel error sensor or load voltage missing system data differ your saved version of the configuration differ from the one in the PLC Can someone help me with this? ore how to check one of the above possible answers? Thanks in advance ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 9/15/2016 9:22:09 AMNew subject after splitting |
|
9/15/2016 9:05 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi Manthos, Is the power-LED on the powermodule on? check the voltage on the powermodule. 24 VDC is needed on the pins 2 or 6 and 0 VDC is needed on the pins 3 or 7.
SIMATIC ET 200S distributed I/O Power module PM-E DC24V (6ES7138-4CA01-0AA0)
hope this helps, regards, |
FCK WAR! |
|
This contribution was helpful to1 thankful Users |
9/16/2016 7:26 PM | |
Posts: 13 Rating: (0) |
Here is the hardware diagnostics off today.
AttachmentHardware_diagnostics_16-09-16.txt (1210 Downloads) |