4/14/2009 8:45 PM | |
Joined: 4/6/2006 Last visit: 1/21/2019 Posts: 604 Rating:
|
Hi, The answer is FB12 and FB13. I think this FAQ will be very helpfull for you: How do you program communication blocks FB12 "BSEND" and FB13 "BRCV" for data exchange on the S7-300? |
Best regards, |
|
4/15/2009 9:19 PM | |
Posts: 8 Rating:
|
Thank you INS, Just after try a bit , now the communication is working Ok between S7-300 and my S7-400 . Just only one thing to keep in mind just if anybody don't knows: According to my communication test between the two PLCs, I found that it's very important to use the FB12 and FB13 from S7-300 side and for S7-400 side we must use the SFB12 and SFB13 . I tried to use FB12 & FB13 in both PLC (300 & 400) and my PLC S7-400 went to STOP. I found the following note in the forum: What should you watch out for when configuring an unspecified S7 connection for data communication between an S7-300 and an S7-400? Thank's again. |
4/16/2009 9:11 AM | |
Joined: 4/6/2006 Last visit: 1/21/2019 Posts: 604 Rating:
|
Hi, Thanks for your feedback. |