Hello Laury; I really recommend you start a new thread next time if you want to have a quick reaction to a new question. Now, the SFC14/15 operate on both the S7-400 and the S7-300, but the size limit might be your problem. S7-300 have a 32 byte limit for the transfer of consistent data with SFC14/15: Could this be the issue? From the manual S7-300, CPU 31xC and CPU 31x: Installation, Operating instructions Rule for 1 byte to 32 bytes data consistency on PROFIBUS DP:
|