http://www.seec.com.tw/product/file/file_673_2164.pdfthese is the manual sir, every time that any diff hmi the user whant to connect to s7 300 plc using the port of mpi the user dont need any setting in the plc even in the netpro sir?by the way sir my using the s7 300 315-1af03-0ab0. |
8/23/2014 4:41 AM | |
Joined: 9/27/2006 Last visit: 3/18/2025 Posts: 12344 Rating:
|
Hello ryan; After looking at the manual you have provided, it would seem Shihlin is expecting you to communicate to the MPI port of the Siemens PLC, using a PC adapter connected to a COM Port on your computer. The PC adapter transforms the RS-232 signal from the PC to RS-485 (MPI standard) and also acts as a gateway to MPI. It should be running at 38.4 kB, with odd parity (see the attached comiplation of your document). PC adapter v. 5.1, latest model manufactured: 6ES7972-0CA23-0XA0 Does your computer have a Com Port (most modern PCs do not)? If not, you would need a PC Adapter USB: 6GK1571-0BA00-0AA0. Once your PC adapter is selected and connected, you will have to select it in the "Set the PC/PG interface" so the PC adapter becomes the connection between youyr PC and the PLC, over MPI. See the following setup information for the USB model: What should you watch out for when installing the USB PC adapter? For information on the standard PC adapter connections, pinouts and more, please look at the following document: PC_TS Adapter - Quick Reference Guide.pdf Hope this helps, Daniel Chartier
|