Hi Leosm You should contact support.energy@siemens.com, as they are responsible for Sicam SAS. Send you SAS project and the logs from ASE. Meanwhile you can try to connect ASE as IEC103 slave and send values to Sicam SAS. Have you checked baudrate, IED address? Are single point informations working? One I connected REL531 to SAS, but without measurements. I remember that problems were always in REL side, as one must configure everything with logic blocks. Mike J |