Hello all Has anyone tried the T104 communication between SICAM SCC station and SICAM SGU ? Is there any manual for this application case? Many thanks |
3/23/2015 3:20 PM | |
Joined: 10/9/2007 Last visit: 9/5/2024 Posts: 1249 Rating: (115)
|
Hi
yes. In SCC you insert a PAS Driver and a IEC Driver.
|
Energy Automation products: Sicam, Siprotec, Digsi |
|
3/27/2015 9:03 AM | |
Joined: 10/9/2007 Last visit: 9/5/2024 Posts: 1249 Rating: (115)
|
Hi
first you have to add a Sicam IEC Communication Suite to the Tag Manager. Then you open the Toolbox II / SCD Manager to Import the file from Toolbox. If you don't see this Option, reinstall SCC as User Defined and select it You only Need the normal WinCC and SCC configuration licenses. For IEC61850 you Need an extra license to Import the SCD file in SCC.
Mike
AttachmentSCC T104.zip (391 Downloads) |
Last edited by: Mike J at: 3/27/2015 9:04:28 AMEnergy Automation products: Sicam, Siprotec, Digsi |
|
This contribution was helpful to2 thankful Users |