11/15/2022 10:35 AM | |
Joined: 1/18/2016 Last visit: 6/21/2024 Posts: 12 Rating: (0) |
Hello everyone, I'm here today to ask for your help in solving the following issue. I have an IM155-6 PN/2 HF with a TM PosInput1 inside, this module is connected to a Sick incremental encoder(datasheet attached). I have wired it as follows:
Then I tried various configurations(tech object, fast mode, manual mode), but I always get an "ENC_ERROR" or "Incorrect encoder signal" and no values. I'm pretty sure this should be an incremental encoder (A,B,N), not sure about signal evaluation and filter frequency thought; interface TTL and no reaction to N. On the TM I have leds, 5V, 24V, PWR and DQ0 on, the other ones remain off. Strange thing is that when I power on the devices, if I remove the cable between the PLC and the ET200, so it does not receive the configuration from the PLC, I see the encoder signals leds A, B and N changing as I turn the encoder. So I thing I have a conf problem, but I really can't guess what it could be. AttachmentdataSheet_DFS60E-BDAK01024_1036279_en.pdf (441 Downloads) |
Last edited by: AutoGen_2546431 at: 11/15/2022 10:49:02 |
|
11/17/2022 7:59 AM | |
Joined: 1/18/2016 Last visit: 6/21/2024 Posts: 12 Rating: (0) |
Thank you very much. Now it works. |