8/21/2018 10:53 PM | |
Joined: 9/27/2006 Last visit: 4/18/2024 Posts: 12256 Rating: (2664) |
Hello JMain; It is more and more difficult to come by manuals for the S5-150S and S5-150U PLCs. In the following link you will find Chapter 8 of the S5-150S system manual, showing detils of the 6ES5 465-3AA12 analog input module; the 6ES5 465-AA13 you are inquiring about is a direct replacement, so the information should be valid for your situation. However, the manual is only available in German... Analogeingabebaugruppen in Kompaktbauform; Analogausgabebaugruppen in Kompaktbauform; Betriebsanleitung https://support.industry.siemens.com/cs/ww/de/view/21498416 In the screenshot below, you will find the pin assignment for voltage or current measurements on the left, for the PT100 connections on the right. The jumper assignments are described on page 5. Hope this helps, Daniel Chartier |