Hello, I have control system based od D435, with control unit CU320 and some Motor Module and motors (scheme). I can spin motors, but still I have problem with gearing two motors together, getting folowing alarms:
Can you give me advice? Thank you. Vojtech Myslivec, CTU FEE |
4/10/2015 9:27 AM | |
Joined: 5/12/2006 Last visit: 4/17/2025 Posts: 22620 Rating:
Hello, check the Diagnostic Buffer of the PLC if there any Error or go the PLC to STOP? Regards |
4/10/2015 10:40 AM | |
Posts: 8 Rating:
Hello, there is nothing special except typical messages (from STOP to STOP_U, from STOP_U to START ...). |
4/10/2015 10:54 AM | |
better you post the saved diagnostic buffer log here for analyze |
4/10/2015 2:20 PM | |
Posts: 8 Rating:
Ok, sorry, log are in attachment.
AttachmentLogs.txt (608 Downloads) |
4/13/2015 12:48 PM | |
Posts: 8 Rating:
Yes, this is it! Thank You. |