10/28/2014 3:54 PM | |
Joined: 8/27/2010 Last visit: 4/13/2024 Posts: 417 Rating: (37) |
Hi! According withS7-300 module data manual, chapter1.4 "Mechanical and climatic environmental conditions for S7-300 operation": The S7-300 may be operated on following environmental conditions: Temperature: horizontal mounting position: 0°C to 60°C vertical mounting position: 0°C to 40°C Relative humidity 10 % to 95 % Barometric pressure 1080 hPa to 795 hPa //Corresponds with an altitude of -1000 m to 2000 m |
10/29/2014 6:23 AM | |
Posts: 138 Rating: (0) |
Thanks guys, So what i analyze is that upto 60 C i can use the normal modules as far as the installation is Horizontal which is the case in my application. My modules will be safe. I just want to confirm if the attached installation is horizontal. Thanks again guys. Best Regards, |
10/29/2014 10:55 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (715)
Hello, Yes, it's horizontal. You can see that the ventilation openings are pointed to the top/bottom, that's why they can operate in a higher ambient temperature then when mounted vertical, better airflow. Regards, Marcjan |
Problem solved? |
10/29/2014 12:55 PM | |
Joined: 9/27/2006 Last visit: 9/13/2024 Posts: 12282 Rating: (2683)
Hello Hike; To detail Marcjan's correct reply more thoroughly, have a look at this page from the S7-300 CPU installation manual: SIMATIC S7-300 CPU 31xC and CPU 31x: Installation Hope this helps, Daniel Chartier Edit: I just reread the thread, and noticed Olloy had already posted the same information earlier. Sorry for the unnecessary posting. D.C. |
11/1/2014 7:22 AM | |
Thanks guys, It has been really good support from all of you. Now i am clear about it. Thanks again, Best Regards, Hike