4/16/2014 3:08 PM | |
Posts: 55 Rating: (0) |
hello guys i have this 2 error onsimatic dp/dp coupler someone have one ideea? thank you
|
4/16/2014 3:17 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello Go to chapter 6 Table 6-2: DP/DP Coupler - Siemens Industry Online Supportare you sure that the data exchange is completely identical? Example: Master 1 Master 2 8 Byte IN ---> 8 Byte OUT 16 Byte OUT ---> 16 Byte IN |
Last edited by: Ste39 at: 4/16/2014 3:30 PMLast edited by: Ste39 at: 4/16/2014 3:18 PM |
|
4/25/2014 1:28 PM | |
Joined: 9/27/2006 Last visit: 9/23/2024 Posts: 12282 Rating: (2685) |
Hello; You could insertSFC12 in the DP1 PLCprogram to deactivate the call of the DP/DP coupler (until the second DP master is connected, if ever), it would remove the fault on the DP1 side, without affecting the hardware configuration.. Notes for the use of the system function SFC12 "D_ACT_DP" Hope this helps, Daniel Chartier |
9/25/2014 2:38 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
Min_Moderator
|