3/9/2019 11:15 PM | |
Joined: 9/27/2006 Last visit: 12/11/2024 Posts: 12302 Rating: (2692) |
Hello M. Abubaker; The power supply you are pointing to is a 3A P.S. for the S5-115U/F family. You can find its data sheet as part of this manual (chapter 17): https://support.industry.siemens.com/cs/ww/en/view/1086946 Notice that the information on this module states that the fuse is "integral", which means it is a solid-state fuse, installed on the printed circuit board. You can either attempt to open the power supply yourself, find the blown fuse and replace it, or send the unit to Siemens (or a competent repair shop) for repairs. Note that opening the cover of a Siemens module will void the warranty; but for a product is Spare Parts for over 10 years that should not bother you too much... Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 3/9/2019 11:15:57 PM |
|
3/10/2019 7:01 AM | |
Joined: 3/15/2018 Last visit: 12/2/2024 Posts: 25 Rating: (0) |
Hello Mr dchartier This is indeed very helpful. Thank you for your support. |