Hello, This PC adapter get it's powersupply from the conected equipment (like plc) some equipment do not have this supply or wrong cable is used. In that case you must use an external powersupply. alternative is SIMATIC PG/PC - PROFIBUS PC Adapter USB A2 Operating InstructionsA Regards, Marcjan |
Problem solved? |
|
8/14/2013 3:30 PM | |
Posts: 2964 Rating:
|
Hello, This Adapter works with Step7 because you get a 24V supply from the S7300. But when you want to communicate with 840D NCU you need to provide the 24vdc external then only it works... Check this FAQ link http://support.automation.siemens.com/WW/view/en/22821092 Regards, Prakash |
8/16/2013 6:08 AM | |
Posts: 166 Rating:
|
Sir Thanks for ur reply Unable to open FAQ link due to message :"You dont have required authorisation to access this document" - kindly advice what is the reason ? Please confirm if I can use Simatic S7 PC Adapter USB 6ES7 972-0CB20 0XA0by externally providing 24V at pin number 7 and 0V on pin number 2 of 9 pin connector of this adpater Regards, M. Rishikesh |
8/16/2013 7:48 AM | |
Posts: 391 Rating:
|
yes it is possible to use , you have to providing 24V on X121 not on X122 pleas read DOConCD or DOConWEB "Configuring the NCU 4.3 NCU module interfaces" |
8/16/2013 7:55 AM | |
Joined: 4/22/2010 Last visit: 12/15/2022 Posts: 5697 Rating:
|
Hello, You can use this adapter by supplying external power, i have attached the schematics. But to be on the save side: To operate the PC Adapter USB to MPI/DP interfaces which do not have a 24V supply voltage, you can order an external power supply (order number: 6ES7 972-0CA00-0XA0). Regards, Marcjan AttachmentPC_Adapter_USB_conections.pdf (1342 Downloads) |