Hello, Is this running machine or under commissioning? Please study the attached sheet. Check the Input supply at U1, V1, W1. Since your system is PLC, please check PLC logicif the input power is controlled thru PLC. At any case, If this input supply is present, then on infeed unit, GREEN LED i.e. LED no 3 must LIT. Please disconnect the X351 connector & check for GREEN LED status. If not, infeed unit is faulty & needs to be replace/repair. If this GREEN LED is ON, then depeding upon infeed module enable signals output will be ON. HTH. AttachmentC:\Documents and Settings\ntguest\Desktop\Infeed module information.pdf (128 Downloads) |