Hello Raheel, reading
I think you are using the CP342-5 as DP-Master? To get the diagnostic data of your slave you have to use this FC. Please have a look at the documentation S7-CPs for PROFIBUS Configuring and Commissioning chapter 5 descripes the dignostic tool. Within the DP_STATUS at the DP_RECV you will get the information that there are faults at your PROFIBUS network. So you have to read the diagnostic list with DP_DIAG. There you will get the information which Slave got the fault. With this information you could read the Single Diagnostic of the Slave to get the detailed information. Good luck Sabine |
11/10/2009 12:18 PM | |
Joined: 8/25/2005 Last visit: 5/25/2023 Posts: 1161 Rating:
|
Hello Raheel, I'm sorry never worked with this device Searching within the internet I found the following pages from the SIEMENS devision energy. There are manuals published. Hope that one you need will be there. Or contact energy customer support. Power Quality Download-Area Good luck, maybe you could give us some feedback Sabine |