6/30/2015 1:49 AM | |
Joined: 9/27/2006 Last visit: 3/26/2025 Posts: 12344 Rating:
|
Hello Mahmoud; Well, at this point, you should give us a bit more information on the Prolinx gateway you are using in your project. Or select the selected gateway from this Prosoft webpage, go to the Downloads tab and look for the manuals for the gateway and the protocols supported: http://www.prosoft-technology.com/Products/Gateways Then, for the Simocode Modbus connection, look at this Siemens webpage, and open the Manuals and Operating instructions to locate information on using Modbus Function 3 with the Simocode: Modbus RTU Kommunikation in SIMOCODE pro V - Siemens Hope this helps, Daniel Chartier |
6/30/2015 11:19 AM | |
Joined: 12/6/2014 Last visit: 6/13/2022 Posts: 13 Rating:
|
Dear sir, my gateway type is Prosoft 5204SE-MNET-PDPMV1 (attached the manual and the application file). after reconfigured the simocode (slave address 10) to basic type 1, the database memory and the modbus addresses were changed. The new memory address is 408 to 417 The new modbus address for the analogue value is 30206 to 30209 I checked out the simocode logic editor I/O data, and found the running hours ( 3870 h ) were sent to the gateway via the simocode cylic send 4/5 block. I couldn`t configure the FC3 command on the gateway so it maybe solve the problem. Please help as i didn`t get any support from prosoft. Regards, Attachmentapplication files.rar (242 Downloads) |