2/18/2010 4:17 PM | |
Posts: 467 Rating:
|
hello, Please look at the manual of Simocode Pro on page 3-11. Link to download the manual http://support.automation.siemens.com/WW/view/en/20017780 Type of Load You can select whether SIMOCODE pro is to protect a 1-phase or a 3-phase load. For a "1-phase" Type of Load, proceed as follows: • The Internal Earth-fault Monitoring and the Unbalance Protection must be deactivated • Only one of the two cables is to be fed through any through-hole opening in the Current Measuring Module. Phase Failure Monitoring is deactivated automatically. |
This contribution was helpful to
1 thankful Users |
5/19/2014 5:15 PM | |
Posts: 202 Rating:
|
Hi There One cane connect a 1-Ph to the simocode for that you just need to pass only the cable from which the phase curent is flowing through the CMM.
|