12/4/2009 11:56 AM | |
Posts: 1 Rating:
|
Configuration fault & Device Fault appearing when operator panel display goes to default screen. Please find the attached circuit diagram. Details for the problem getting faced. Configuration of the feeder: DOL Starter Current & Voltage Measuring Module, Basic Module Unit 2, 220V AC supply Expansion module with 220V AC supply Earth fault module, Operator Panel. When display setting for return to main display is set to 10 sec or 1Min. Operator panel display is browse to Protection as shown below, after the set time operator panel display goes blank & basic module LED Device & General fault turns red flashing. To reset the above conditions aux supply to simocode needs to be switched OFF. AttachmentSIEMENS DOL Feeder 90kW.pdf (302 Downloads) |
12/10/2009 1:12 PM | |
Posts: 467 Rating:
|
Hello, this is an unknown behavior. I would suggest to go in contact with Technical Assistance and provide the current parameter setting (sdp file) and describe this behaviour. The specialist from technical assistance can investige this behavior. Perhaps it is possible to reproduce this behaviour and find out the cause of them. mailto:technical-assistance@siemens.com kind regards |
Last edited by: LesPaul at: 12/10/2009 1:12 PM |
|