Is it possible to reduce the start up time where this protection is in-active (in our case 10 sec for a class 10 motor)? Thank you, AJ |
4/10/2017 3:05 PM | |
Joined: 5/17/2010 Last visit: 2/17/2025 Posts: 226 Rating:
|
Hello AJ, I thought your request was on Stalled Rotor protection which can be additional set to the current limit monitoring features. So usually it does not make sense to have this current-based monitoring features active while motor startup because it would trip due to high startup current. Only the motor protection which is a delayed monitoring feature is active. It is not possible to change current limit monitoring to ON mode but it is general possible to deactivate this startup override/faid-out of current-based monitoring features by change of "Type of Consumer Load" from "Motor" to "Resistive Load" because a Resistice Load does not have higher startup current. Is this what you are looking for? Or why do you not want to have the suppression of current-based Monitoring functions while motor startup? With best regards Michael |
------------------------------------------------------------------------------------------------ |
|