8/4/2021 5:43 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello chatjokey1, Welcome to forum. You should have open this topic in DC converters SIMOREG product conference which is the correct one. BTW I request Moderator to transfer this topic. Now to your query, from your description, it looks like problem trigers when your motor run in field weakning mode.(please check & confirm, since relevant data is not available) & it seems that this machine is installed in your shop recently, I suggest you to please check below points. 1. Please confirm drive parameters are as per original/earlier values & are OK. (especially ramp up & ramp down time) 2. Please check head stock lubrication & gear mechanics. 3. Please note F04 - phase failuer or electronics supply failure when drive enable is present & F19 - Armature circuit interupted e.g. fuse blown, phase failure, EMF set p77 too high, line undervoltage etc. etc. As such, I suggest you to check input supply cable ( sq. mm) specification - check if it is adequate to handle application demand, loose connections in lugs, fuse base & fuse etc. etc. 4. Please carry out Auto optimistaion of drive & motor if all above points found OK. HTH . |
Last edited by: PISCEAN 2010 at: 08/04/2021 08:05:00 |
|
8/4/2021 8:53 PM | |
Posts: 26 Rating: (0) |
There is one problem. I cant calculate because i dont know some data. please see attached. The present parameters almost simular with the factory settings and set values in the manual. The difference are: P30 (digital offset adjustment of speed controller) =-1 P31 (Speed controller P-gain) = factory setting is 5,0 , set value is 18, but the present value is 7 P32 (Speed controller integral-action time) = factory setting is 1,0 , set value is 0,5, present value is 0,5 P39 (Positive current limit value 1) = factory setting is 120, present value is 95 P40 (negative current limit value 1) = factory setting is 120, present value is 95 P41 (Positive current limit value 2) = factory setting is 120, present value is 90 P42 (negative current limit value 2) = factory setting is 120, present value is 90 P48 (Speed related current limitting threshold) = factory setting is 100 , set value is 76, present value is 76 P49 (Current limit value at maximum speed) = factory setting is 100 , set value is 81, present value is 84 P62 (Ramp up time for current setpoint integrator) = factory setting is 0 , set value is 85, present value is 85 P64 (Current controller P-gain) = factory setting is 0.05 , set value is 0.31, present value is 0.31 P65 (Current controller integral-action time) = factory setting is 50 , set value is 16, present value is 16 P66 (Precontrol R component with intermittent flow) = factory setting is 0 , set value is 31, present value is 31 P67 (Precontrol R component with continuous flow) = factory setting is 0 , set value is 31, present value is 31 P68 (Continuous current boundary) = factory setting is 10 , set value is 19, present value is 19 P71 (Rated motor current/rated current) = factory setting is 80 , set value is 81, present value is 75 P76 (Rated field current (motor)/field current limit (conventer)) = factory setting is 50 , set value is 42, present value is 76 P77 (e.m.f. setpoint) = factory setting is 340 , set value is 352, present value is 348 P87 (selection of operating mode for restart) = factory setting is 32 , present value is 31 P88 (selection of operating mode for automatic field current reduction) = factory setting is 0 , present value is 1 P90 (Selection of operating mode for field) = factory setting is 02 , set value is 00, present value is 10 E01 (System voltage speed setpoint) = factory setting is 100 , set value is 90, present value is 90 E57,58,59 (Nmin3, Nmin4,Nmin5) = factory setting are 0 , present values are 0.5 E70 (selection of operating mode for torque control function) = factory setting is 00 , present value is 01 |
8/5/2021 1:56 PM | |
Posts: 26 Rating: (0) |
one more video with parameters 1-20 while spindle running
|
8/5/2021 3:40 PM | |
Posts: 26 Rating: (0) |
change drive on the simular. I got 3 of these. the same. doesn't stop. f04 on low and f19 on high rpm |
Last edited by: chatjokey1 at: 08/05/2021 15:57:22 |
|
8/6/2021 5:43 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please modify/change P77 value to 375 & check. |
8/6/2021 12:47 PM | |
Posts: 26 Rating: (0) |
worse. 200 rpm f04. |
8/6/2021 1:15 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
1. Please check field current value & report here. 2. Please conduct speed optimisation only by setting p51= 3. |
8/6/2021 2:43 PM | |
Posts: 26 Rating: (0) |
please see attached. 50 drive rpm. edit. its ~. dont have Dc. |
Last edited by: chatjokey1 at: 08/06/2021 15:13:39 |
|
8/7/2021 5:05 PM | |
Posts: 26 Rating: (0) |
Have measured dcA. pluged in here - please see attached. |
8/10/2021 5:49 PM | |
Posts: 26 Rating: (0) |
have bought new tool. 2,41-2,43 A |
8/11/2021 5:52 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Field current 2.41-2.43 at what set point? Please read my last post & conduct speed & field optimisation & check. |
8/11/2021 12:56 PM | |
Posts: 26 Rating: (0) |
0.77A - no rotation 2.4 A - 0-1450 drive rotation then it get lower. 2.2 - 1580 1.8 - 1728 1.1 - 2160 0.72 - 2880 |
8/11/2021 1:09 PM | |
Posts: 26 Rating: (0) |
no its not. can I use this? see attached. |
8/11/2021 1:31 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Yes. But I suggest you to measure armature voltage by DC multimeter also. |
8/12/2021 5:15 PM | |
Posts: 26 Rating: (0) |
may be its better to start from the begining? |
8/14/2021 5:04 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
1. Set p16 =3 p17 = 3 & check. 2. Check winding resistance between wire no 431 & 432 & report. |
8/14/2021 12:15 PM | |
Posts: 26 Rating: (0) |
1. 0.03? or 3.00? 0.03 - 100rpm - f04. worst. 2. attached |
Follow us on