4/18/2020 4:18 AM | |
Joined: 10/17/2007 Last visit: 3/19/2023 Posts: 3276 Rating:
Attached is 840D Diagnosis manual--all alarms and how to fix. Actually I have no idea about hydraulic control axis, with the help of the manual, you can think, why these error happen. why they not happen when machine was new. some parts aged , if you have more than one control card, switching to test. make sure card is good. then check re replaced valves , hydraulic motor? feedback signal cables. all inside your drawing need test I just have a idea--you have X2 & X3 axis all alarm same? so you can look for some common factors such as power? control card.... AttachmentDA_1102_en.pdf (143 Downloads) |
Last edited by: nulizhang at: 04/19/2020 00:31:39look for some common factors Please Help me to understand your question! |
4/18/2020 7:02 AM | |
Joined: 4/23/2010 Last visit: 4/2/2023 Posts: 8026 Rating:
Hello HER00, Alarm 25080 - Axis position monitoring, i.e. CNC checks if the axis comand position is reached as per limits set in axis MD 36000. 36010 within time set in MD36020. Since you mentioned it is hydraulic system, please check if it is for axis clamping or for axis motion. Also check the hydraulic system pressure, flow control etc. Also please check, hydraulic valave coil connection, coil resistance, supply at coil end. Some loose connection or coil open may be the culprit. HTH. |