Joined: 8/25/2006 Last visit: 4/27/2024 Posts: 2203 Rating: (277) |
When you see "Online" in parameter table, this means that parameter can be changed in all operating states. "Offline" means that parameter can be changed in operating states of ≥o1.0. You may see the description of all operating states of the drive in parameter r001.
Can you change P044 to some another value? Try to change this parameter from PMU or OP1S. How your PC with DriveMonitorconnected to the drive, directly to the X300 on front panel of drive or through Profibus?
ADB - is an adapter board, which is need (with LBA - local bus adapter) to install CBP2 (Profibus board). ADB and LBA need not to be parametrized or configured. When you use profibus board (CBP2) you need to set a fewnumber of communication parameters. Read about this in the manual, chapter 7.7.2. |
11/2/2010 12:12 PM | |
Joined: 8/25/2006 Last visit: 4/27/2024 Posts: 2203 Rating: (277) |
All information is available in the manual. Description of F048 is on the page 450. F048 belongs to the encoder connected to the terminals X173:28,30, you may see this on the function diagram sheet G145 (page 247 in the manual). |