Hello, First of all you should use the GSD file comming with Sinamics memory card. Open the memory card with your PC and CF card: \\SIEMENS\SINAMICS\DATA\CFG\CBE20GSD.ZIP. Example: http://support.automation.siemens.com/WW/view/en/25166781 Best regards, Hristo Mihalev |
11/18/2010 11:30 AM | |
Joined: 9/15/2010 Last visit: 9/26/2022 Posts: 24 Rating:
|
Hristo thank you for the reply, GSD file was the first step to establish active connection. My problem was that proces image on sinamics was not the same as one in S7 HW, so after modifying PZD on the drive side and in HW comunication was OK. In attachment I will put some pictures of HW in case that any body in the future will have the same problem. Regards, Kreso AttachmentSinamics S120 - HW S7 414-3 DP.zip (140 Downloads) |