7/24/2013 9:13 AM | |
Posts: 1064 Rating:
|
take a look at sfc 51 RDSYSST this shoul ddo what you want |
This contribution was helpful to
1 thankful Users |
7/24/2013 9:55 AM | |
Posts: 1547 Rating:
|
Hi, there are many ways to catch the goal: 1. using report system error --> try this FAQ: SINAMICS, SIMATIC: How to use the SIMATIC function "Report System Errors" Diagnostic also with HMI. 2. Using the OB 86 which will be called if aslave will fail or be disconnected. Problem this OB will be only called in case of a fault in other case there is no call, because everything is fine. 3. Using SFC13 Reading DP-Slave norm diagnostic information from salve and read operational state. This call can be used in OB1 to all salves (Siemens or not Siemens),because it is reading the standard diagnostic from PROFIBUS DP specification. |
This contribution was helpful to
3 thankful Users |
7/24/2013 10:07 AM | |
Posts: 1064 Rating:
|
anothe rthing if you have wincc flex using fb125 is nice take a look at this thread /tf/WW/en/Posts/20189 |
This contribution was helpful to
1 thankful Users |