Not everything can be seen in your screenshot. Please upload your program as a ZIP file.
|
11/19/2020 8:41 AM | |
Posts: 6 Rating:
|
As requested. Please see attached. Works fine when simulating in LOGO SOFT. But once i upload to LOGO BASE UNIT it jumps to over 65000.
AttachmentCRC STEAM LOOP CONTROL2 FORUM.zip (84 Downloads) |
11/19/2020 8:59 AM | |
Posts: 6 Rating:
|
This is the readout I get on the LOGO unit when i Increase the setpoint by 1 and then it counts up by 1 increment from there again. |
11/19/2020 9:12 AM | |
Joined: 12/18/2014 Last visit: 12/3/2023 Posts: 31538 Rating:
|
I changed the counter B002 to a other counter (B011). After that I changed the counter B011 back to other counter (B002) back. Then works the counter in the real LOGO! correctly. In attachment the corrected diagram. I don't know why this fault so is. Only Siemens can say something to this. AttachmentCRC STEAM LOOP CONTROL2 FORUM_V2.zip (85 Downloads) |
Last edited by: ixo65 at: 11/19/2020 09:12:32 |
|
This contribution was helpful to
1 thankful Users |
11/19/2020 9:14 AM | |
Posts: 6 Rating:
|
Thanks IXO i will give it a try. Much Appreciated indeed. Have a great day and see you when i see you. |
11/19/2020 9:16 AM | |
Joined: 12/18/2014 Last visit: 12/3/2023 Posts: 31538 Rating:
|
I wish you also a nice day ... |