3/3/2018 9:10 AM | |
Joined: 1/17/2013 Last visit: 9/20/2024 Posts: 1104 Rating: (6) |
Dear PISCEAN 2010, The problem from NC contact of infeed magnetic have problem. I have changed new one and F7300 removed. I need to know more as previous picture. What is Line contactor enable ? Is it hardware or software ? What is Line contactor enable IN and OUT signal ? What is Infeed enable OUT signal ? Best Regards, Vorapob |
Best Regards, |
|
This contribution was helpful to1 thankful Users |
3/3/2018 9:44 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, Nice to learn your problem is solved. In your attached picture, Line contactor enble block is software & physical wiring of contactor NC is hardware. Line contactor enable IN OUT signals are DI/DO inacse of hardwiring where as in case of profidrive/profinet communication, it is bit tranfer via control word & status word. Infeed enable output signal indicates close loop operation completed & needs to configure in further logic. Please download & refer SINAMICS S120/S150 manual, chapter Function diagram, 3.10 sequence control to understand answers of your questions. HTH. |