4/16/2016 2:23 PM | |
Joined: 11/21/2007 Last visit: 3/14/2024 Posts: 2323 Rating: (307) |
Hello Friends This is a very good FAQ document available from Support to understand , and resolve common faults in SINAMICS DCM ( 6RA80 ) Drives. Several different ways of performing diagnostics on the SINAMICS DCM 6RA80 are described in the FAQ. You do not have to read the entire text, only the item relevant to your problem. This permits you to perform the necessary preliminary investigation, which you can then discuss with Technical Support Hope this helps Cheers Navnag AttachmentSINAMICS_DCM_Fault_Diagnosis.pdf (2080 Downloads) |
There is no such thing as the last bug in a program |
|
4/16/2016 5:37 PM |
|
Posts: 64 Rating: (0) |
Do you have the same document for simoreg 6RA70 ? |
4/16/2016 5:47 PM | |
Joined: 3/28/2015 Last visit: 5/25/2024 Posts: 721 Rating: (213) |
Hello, |
Eng.Mohamed Ibrahim |
|
This contribution was helpful to1 thankful Users |
11/20/2016 7:31 AM | |
Posts: 2 Rating: (0) |
SIR,I am set motor max speed 1800rpm in p2000=1800 but same fault f60056,r949-9 pl help |
Last edited by: adity1 at: 11/20/2016 7:32:07 AM |
|
11/20/2016 8:07 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, Please download manual, refer chapter 8 commissioning, which will give you detail information. e.g. how to commissioning, how to eneter all motor data correctly etc. etc. |
4/1/2018 12:24 AM | |
Posts: 1 Rating: (0) |
|
4/1/2018 5:15 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, F9000 to F12999 are reserved & I suggest you to contact your nearest Siemens service support or raise support request. |
Follow us on