Hello everybody! I would appreciate anyone's help regarding this issue. I'm using AI X177.25-26 as a main speed reference for DCM drive (6RA8078-6DV62-0AA0). The problem is when I have 0V for speed reference, DCM registers about 2mV (possible some noise) casing drive to move very slow which I want to avoid. Is there any way to make a kind if dead band (with 10mV) around zero speed reference (0V) or any other way (making AI not listen signal below 10mV) to avoid this. Switch On/Off1 and Enable operation are active all the time. Thanks in advance. Marko ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 2/5/2019 11:16:50 AMNew subject after splitting |
|
2/5/2019 12:18 PM | |
Joined: 8/25/2006 Last visit: 12/13/2024 Posts: 2211 Rating: (280) |
Hello. 1. Free function blocks: LVM + NSW 2. FD 8020, p50596=52011, p50597=0, p50376-p50378 as required, p1142=53025.3 |