7/17/2018 12:24 PM | |
Joined: 7/17/2018 Last visit: 5/27/2021 Posts: 3 Rating: (0) |
Good afternoon, dear experts! We have a configuration with one CPU 314 2DP and Sinamics DCM 6RA8025-6DV62-0AA0. We need to connect them via Profibus DP. The task is to receive some extra data from the Sinamics DCM comparing to the Standard Telegram 1 PZD-2/2, so we have chosen telegram 352 PZD-6/6. Telegram 1 PZD-2/2 functioned OK, and we both successfully sent control word and setpoint and received status word and speed. But after changing to the telegram 352 PZD-6/6 a problem occurred. We still can send and receive PZD1 and PZD2, but we are unable to do that with PZD3-6. Our analysis of the situation showed that the problem is in the source and offset (see attached screenshots) of the PZD3-6 of the telegram 352. They are equaled to 65535 instead of M for the source and 4 to 10 for the offset. The same problem is for the bus address PZD receive (r2074). It is equaled to one for the PZD1-2 and 65535 - for the PZD3-6. All parameters in the Starter Expert list, which are responsible for this (r2074, r2075), are read-only. The question is how to change the sources and offsets for the PZD3-6? Thank you very much. Best regards, Vladislav Petrov. AttachmentScreenshots.pdf (613 Downloads) |
Last edited by: Vladislav92 at: 7/17/2018 12:38:39 PM |
|
7/17/2018 12:50 PM | |
Joined: 8/25/2006 Last visit: 1/17/2025 Posts: 2211 Rating: (280) |
Hello. Have you changed telegram configuration also in HWConfig of CPU314? |
7/17/2018 1:05 PM | |
Joined: 7/17/2018 Last visit: 5/27/2021 Posts: 3 Rating: (0) |
Dear KSN, Yes, we have changed the configuration of the telegrams in HWConfig of CPU314 (see attached screenshots - page 1). We even tried another configuration in this config (see attached screenshots - page 2). But everything was in vain. Best regards, Vladislav Petrov. Attachmenttel_conf_cpu314.pdf (594 Downloads) |
7/17/2018 1:37 PM | |
Joined: 8/25/2006 Last visit: 1/17/2025 Posts: 2211 Rating: (280) |
In Starter you have configured telegrams for two drive objects: 1. Drive - PZD 6/6 2. CU - PZD 2/2 You should make the same configuration in HWConfig. Look at screens. Or you should select zero telegram lengths in Starter for CU. Attachmentscreen.zip (579 Downloads) |
This contribution was helpful to1 thankful Users |