Hello, do you use standard telegramm 2? What is p2000 (reference speed) and your setpoint in the PLC? Example: P2000 = 3000rpm and you want to run with 1500 rpm. So you have to send 50% = 2000 0000 HEX from the PLC (100% = 40000000HEX for DWORD or 100% = 4000 HEX for WORD) application example: http://support.automation.siemens.com/WW/view/en/58820849 Of course there are further possiblities like mechanical problems - but than you should get error messages. But I don`t know your parametrization. Maybe you can send us some screen shots of the speed setpoint channel (STARTER pictures). Regards Zako |