You have to send a control word (and a set point) like described on page C-25 (page 54 in PDF) in the USS specification (https://support.industry.siemens.com/cs/ww/en/view/24178253). When you change from 047E to 047F the drive will switch on (if it has no active fault) and if you send 047E again it will switch of (after it reached 0 Hz) You can reverse the drive by negating the setpoint. 16384 is the speed defined in p2000 of the drive. -16384 is the same speed, but in the other direction. |