7/26/2013 12:21 PM | |
Posts: 61 Rating:
|
Here it the Siemens Installation manual for Power Module PM240 where is written that this inverter can work on IT system, but we need to disconnect "internal Y capacitors". Is this mistake or it works in special cases. Best regards, G.P. AttachmentG120_PM240(2).pdf (460 Downloads) |
7/26/2013 12:33 PM | |
Joined: 5/12/2006 Last visit: 2/6/2025 Posts: 22526 Rating:
|
Hello, in the installation manual 07/2009 is a picture on side 37 http://support.automation.siemens.com/WW/view/en/52593268 Regards Christoph |
This contribution was helpful to
1 thankful Users |
Follow us on