hello is it correct to use PM230 IP20 for conveying application ? |
2/15/2013 3:28 PM | |
Joined: 10/11/2006 Last visit: 1/22/2025 Posts: 5985 Rating: (824)
|
Hello, normally the PM230 is not designed for conveyors. Its for pumps and fans. At a conveyor there could be always some generatoric shares which could creates Vdc overvoltage at a PM230. Following an example with a G120D. But also PM240 would be a good solution. http://support.automation.siemens.com/WW/view/en/58399364 |