Joined: 4/28/2015 Last visit: 9/20/2022 Posts: 1278 Rating: (300) |
Hello, the correct (and only) way is to commission your S120 with STARTER/SCOUT and use a GSDML file for the communication configuration in TIA Portal. You can either set up the GSDML file (with all telegrams and DOs) manually in TIA Portal or you use the script which can be executed in STARTER/SCOUT and generates a specific GSDML file of your config in STARTER. This file then can be installed to TIA Portal and you can ensure that the config is really the same as in STARTER. https://support.industry.siemens.com/cs/ww/en/view/92022677 (Or you go to TIA / Startdrive V15, there you have S120 included) |
Last edited by: RB91 at: 06/12/2019 07:18:32Best regards, |
|
This contribution was helpful to1 thankful Users |
6/12/2019 3:40 PM | |
Joined: 4/20/2017 Last visit: 9/17/2024 Posts: 81 Rating: (6) |
Thank you for your reply. It helped me!
|