9/3/2016 7:22 AM | |
Posts: 1529 Rating: (202) |
That would be static electricity. Non-conductive surfaces do not conduct electricity. To satisfy yourself, check resistance to ground. It should be huge. |
9/3/2016 7:42 AM | |
Joined: 4/2/2014 Last visit: 1/25/2024 Posts: 52 Rating: (1) |
If it is static electricity then what would be voltage value ?? Here checking with meter it shows 43 Volts. Regards, M |
9/3/2016 10:26 AM | |
Joined: 4/2/2014 Last visit: 1/25/2024 Posts: 52 Rating: (1) |
Is it possible to have induced voltage in non-metallic body of drive ?? please refer attachment & suggest.. |
9/3/2016 10:45 AM | |
Posts: 1529 Rating: (202) |
Non-metallic? No. However, it looks like you are covered with conductive dust. Drive is going to fail soon when something arcs. |
9/3/2016 12:59 PM | |
Joined: 4/2/2014 Last visit: 1/25/2024 Posts: 52 Rating: (1) |
The reading was taken in AC.. need some guidance to overcome the issue.. |
9/3/2016 1:04 PM | |
Posts: 1529 Rating: (202) |
That's what I'm seeing. Capacitor in the making with a conductive film. Drive goes poof soon. |
This contribution was helpful to2 thankful Users |