1/21/2019 1:10 PM | |
Joined: 10/11/2006 Last visit: 9/30/2024 Posts: 5909 Rating: (805)
|
Hello, compare the setpoint on PLC and on Drive. It is possible to use the trace tool. May be the reference values are wrong. P2000 - P2003 Page 863 https://support.industry.siemens.com/cs/ww/en/view/109760366 Description:Sets the reference quantity for velocity. All velocities specified as relative value are referred to this reference quantity. The reference quantity corresponds to 100% or 4000 hex (word) or 4000 0000 hex (double word). Dependency:Refer to: p0500, p2001, p2002, p2003, r2004 Application on Drive: Winder https://support.industry.siemens.com/cs/ww/en/view/38043750 Further Application: https://support.industry.siemens.com/cs/ww/en/view/109757232 |
With best regards, |
|