8/2/2018 1:02 PM | |
Joined: 2/7/2018 Last visit: 3/14/2023 Posts: 181 Rating: (30)
|
Hello, To move the Axis you should use “Positioning axis technology object” combined with telegram 105. For additional requirements on the torque control is telegram 750 required. Then you will be able to work with the “MC_torque Commands”, where you are able to control the torque. You will find further information about the “MC_torque Commands” in the motion control manual starting on page 417. https://support.industry.siemens.com/cs/ww/en/view/109749262 Hints: Telegram 750 is a supplementary telegram for torque control with the following data: When using a technology object, you can read out the actual torque value in the variable"PositioningAxis_1".StatusTorqueData.ActualTorque. First the supplementary telegram 750 is set in the HW configuration. Then the technology object is still permitted to take into account the torque data as additional data. This must be enabled in the TO configuration under "Data exchanged with the drive -> Additional data" with the check mark "Torque data". Please check the screenshot attached. Your Technical Support for SINAMICS S210 |
Last edited by: TechSupport SINAMICS S210 at: 8/2/2018 1:02:52 PM |
|
This contribution was helpful to2 thankful Users |
7/25/2019 12:00 PM | |
Joined: 8/16/2014 Last visit: 7/25/2024 Posts: 10 Rating: (0) |
Hello SandstromDJ, were you succesfull with S210 solution for you application. I have similar application. Thank you |
12/8/2020 3:18 PM | |
Joined: 1/17/2013 Last visit: 10/3/2024 Posts: 1105 Rating: (6) |
Dear Technical Support for SINAMICS S210, Can drive configuration more than one telegram ? How to programming it ? Best Regards, Vorapob |
Best Regards, |
|
12/8/2020 4:02 PM | |
Joined: 2/7/2018 Last visit: 3/14/2023 Posts: 181 Rating: (30)
|
Hi Vorapob, yes, the SINAMICS S210 can work with more than one telegram. Please see the overview at following URL: https://support.industry.siemens.com/cs/ww/en/view/109781874/130705276939 To change the telegram you need to go to the HW-config of the drive. If you go to the properties of the Profinet-interface you can see the topic "Telegram-configuration". There you can change the send and recieve telegram. Additionally the telegram has to be changed in the configuration of the technology object. Best regards Technical Support for SINAMICS S210
|