Please, i need a help! one of my siemens SINAMICS V20 Inverter stopped working and was displaying F1 with a Red blinking light. how do i correct/reset the fault? with part NO: 1P 6SL3210-5BB17--5UV0 see attach the drive detail will be glad to receive immediate solution Regards / Paul ------------------------------------------------------------------------------------------ |
Last edited by: Paulnupel at: 3/23/2018 1:45:04 AMLast edited by: Jen_Moderator at: 3/23/2018 2:48:29 PMNew subject after splitting |
|
3/25/2018 1:12 AM | |
Posts: 2 Rating: (0) |
please Moderator assist me with an answer to my question |
3/26/2018 11:02 AM | |
Joined: 10/11/2006 Last visit: 12/5/2024 Posts: 5960 Rating: (820)
|
Hello, did you have a look in the manual: Fault: F1 Overcurrent Cause: • Motor power (P0307) does not correspond to the inverter power (r0206). • Motor lead short circuit • Earth faults r0949 = 0: Hardware reported r0949 = 1: Software reported r0949 = 22: Hardware reported Remedy: Check the following: • Motor power (P0307) must correspond to inverter power (r0206). • Cable length limits must not be exceeded. • Motor cable and motor must have no shortcircuits or earth faults. • Motor parameters must match the motor in use. • Value of stator resistance (P0350) must be correct. • Motor must not be obstructed or overloaded. • Increase ramp-up time (P1120) • Reduce starting boost level (P1312) If this does not solve your problem, or if you need some additional, we recommend to contact the technical support: https://support.industry.siemens.com/my/ww/de/requests/#createRequest |