Dear TechTeam, Pls advise what could be a problem with my Sinamics V20. I can read Ok all modbus map from V20. I ran Cn011 macro to enable command and setpoint via modbus. then set P2014[0] USS / MODBUS telegram off time [ms] to 0, to avoid error of comm. timeout fault. I use modbus probe tool like Modbus Poll , which allows to wirte single words to any holding registers as well . Then I write 47Eh to STW , then freq. setpoint to HIW , then 47F to STW. And nothing - motor won't run. On BOP, I can see changing setpoint. But actual speed = 0, In current speed screen of BOP, Hz just blinking as 0.0 (actual) --> 28.3 Hz (setpoint.) so far no idea, thinking in this direction:
thanks, ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 10/6/2016 3:03:19 PMNew subject after splitting |
|
10/6/2016 4:57 PM | |
Posts: 5225 Rating: (1196) |
Good Morning. What is going to be the master in the network?.. A while back I was networking an S7-1200 and several V20 drives on a Modbus network. The Siemens provided example was of great help - Even if you do not have the same configuration have a look at the example... or specifically look at the PDF document that goes with it. There is descriptions of of all elements of making the control work (include hardware, software, signalling, ...). For your problem - have a look in the PDF document about the description of how the user activates the drive to run. Notice all the individual control bits that should be switched. CAREFUL - some needs to be TRUE while some needs to be FALSE. You will find this information in a picture about the HMI usage - it is not spelled out that those bits should be ON/OFF. With this information you will know what control bits the MASTER in the network should trigger for the result you need. I hope this helps you. Good luck. |
10/8/2016 9:20 AM | |
Joined: 4/23/2010 Last visit: 11/23/2024 Posts: 8092 Rating: (878) |
Hello eam_rts, Set P0840[0] = - & check. |
3/20/2018 10:16 AM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (173) |
New question published by Mike Troshin is split to a separate thread with the subject When start the drive with DI1 the motor rotates with an old frequency value and shows the old value on the BOP. Best regards |