Hello Aikka, if r1114 is at 0.0, please check your parameterized setpoint source first. During commissioning you have to choose the selected setpoint source in p1000, see also chapter 5.5.2 quick commissioning in the V20 operating instruction manual. Otherwise the default frequency setpoint source “MOP” is used. https://support.industry.siemens.com/cs/ww/en/view/109799545 Another reason why r1114 could be 0.0 even though you are sending a setpoint other than 0 could be the setting of p1110 to inhibit negative frequency setpoints, for example when sending negative setpoint values. |