Dear TommyT15629, I would recommend use first the connection makro CN011 for Modbus RTU. Afterwards change p0700 command selection from 5 to 2 (terminal as command). Then allocate the functionality to the DI (Cn002 might be a good example) Please find section 5.5 in the V20s manual https://support.industry.siemens.com/cs/ww/en/view/109824500 |