Any body pls help.... |
5/6/2014 7:43 AM | |
Posts: 4 Rating: (0) |
you can use the MM4 parameter list manual for F0002 check. link: https://support.automation.siemens.com/CN/llisapi.dll?aktprim=0&lang=en&referer=%2fCN%2f&func=cslib.csinfo&siteid=csius&treeLang=zh&groupid=18886884&extranet=standard&viewreg=CN&nodeid0=10804928&objaction=csopen Description as below: F0002 Overvoltage STOP II Quit Refer to F0001 Cause - DC link voltage (r0026) higher than the overvoltage threshold (refer to parameter r0026) - ground fault Diagnosis & Remedy Please check the following: - is the line supply voltage within the permissible range? - has the DC current DC link monitoring been enabled (P1240) and correctly parameterized? - extend the deceleration ramp (ramp-down time P1121, P1135) - remove the ground fault - is the required braking power within the permissible limits? NOTE - a higher moment of inertia requires longer deceleration times; if required, use a braking resistor. - overvoltage can either be caused by an excessively high line supply voltage or by the fact that the motor is generating (regenerative mode). - the motor can be generating as it is decelerating quickly or due to the fact that an active load is driving the motor. |