Hello ptamas
you can use ET200U stations as "real' Profibus DP Slaves on an S7 as long as they support "DP-Norm Protocol" (which the 318-8MB11 does unfortunately not, so it depends on how your ET200U are). Beloware a fewFAQ's links for that subject which should help you in determing if it is possiblefor not: Coupling ET200U DP (6ES5 318 8MB12) to an S7 master Various PROFIBUS DP-Protocols for IM 318 Configuration of certain DP slaves is not possible in COM PROFIBUS V5.x(note, also applies to usage in Step 7) As for the Festo I/O station I'm afraid to say that you will need to check with Festo if they have a GSD file for it and if it can be used as a DP Slave. I hope this helps |
Last edited by: fritz at: 4/22/2010 5:19 AMCheers |
|
4/22/2010 11:33 AM | |
Joined: 10/7/2005 Last visit: 3/20/2025 Posts: 3042 Rating:
|
Hello ptamas I only have a couple of"nasty" possible solution and both require the purchase of more S5 gear. 1.) Search theweb for 318-8MB12 or 13 IM's to replace your 318-8MB11 (you'll still need to replace the Festo I/O stationthough). 2.) Add an IM308C to your S5, make it a DP Slave of your S7 and have some very simple "Load/Transfer" logic left in your S5 CPU for data marshallingbetween thetheS7 andtheexisting SINEC L2 DP bus (i.e. the S5 becomes your "protocolconverter"). |
Cheers |
|