Is this a single-phase motor? Typically reversing contactors work for three-phase motorsby helping reverse the phase of two legs of the 3 phases, and include some mechanical interlocking (to prevent both forward and reverse contacts from being closed at the same time). In my experience,single-phase motor reversal is normally a one-time event - done at installation. |
science guy |
|
7/16/2012 9:47 PM | ||||||||||||||||||||||||||
Joined: 4/22/2010 Last visit: 12/15/2022 Posts: 5697 Rating:
|
Hello, I think you should read the schematic like this. For 230 V motor running counter-clockwise (ccw) connect L1 to T1 Connect L2 (N) to T4 and T5 T2, T3 and T8 should be connected together CW= clockwise an you should make the connections as shown in table. So you have to swap T8 with T5 for changing direction.
Regards, Marcjan |
|||||||||||||||||||||||||
Last edited by: Marcjan at: 7/16/2012 10:06 PMLast edited by: Marcjan at: 7/16/2012 9:51 PMProblem solved? |
||||||||||||||||||||||||||
7/16/2012 10:04 PM | |
Posts: 4 Rating:
|
Yes this is a single phase motor. It runs a commercially available tubing bender and needs to go forward and reverse. Existing contactor/overload was discarded, no wiring diagram made. OEM is no longer in business. Siemens sells the 43CP12FB (catalog shows this number, Industry Malls lists it as US2:43CP12BF) as a single phase reversing contactor. |