4/22/2012 6:32 AM | |
Joined: 3/21/2006 Last visit: 3/2/2023 Posts: 10221 Rating:
|
Hello, All the info concerningconfigur ADI4 and PP 72/48 I/O to 840DE sl is there. Best regards, Hristo Mihalev
|
4/22/2012 7:09 AM | |
Joined: 3/28/2007 Last visit: 3/11/2023 Posts: 40 Rating:
|
Thank You |
4/22/2012 11:41 AM | |
Posts: 2964 Rating:
|
Hello.... Adding to the above point....Profinet is only avialble with NCU 720.2 PN and NCU 730.2 PN... If you have your tool box cd.... you have the GSD informations.... Check it and revert back... Regards, Prakash |
5/4/2012 10:32 AM | |
Posts: 63 Rating:
|
Also make sure that you are using Step7 5.4 SP5 sw for configuration |
5/21/2020 9:58 AM | |
Joined: 6/17/2018 Last visit: 2/22/2023 Posts: 4 Rating:
|
the actual link https://cache.industry.siemens.com/dl/files/160/108840160/att_825124/v1/GPPA_0310_en.pdf the document relates to 828DSL. For control type 840DSL change bit 0 of byte m+1 to 0. So 0 is for 840DSL and 1 is for 828DSL. This setting will allow you to have full analog resolution at output (26214 output units) The gsd file for PN typeis attached. kind regards Attachment62332440_pp72_48-pn.zip (77 Downloads) |